Thanks for this. My dealings with them so far have been good but will keep this in mind.
How did you get a view on what you thought the right flow temperature? Presumably this meant you weren’t happy with the radiator upgrades they were suggesting. Just did the heat geek quote as comparison and they are quoting a lot more.
We don’t need planning permission so that side is simpler for us.
-
45deg flow temp design at -2deg outdoor temp is completely fine, I don’t know why @Soul was put off by that honestly?!
All the big energy companies design their systems to a 45/50deg max flow temp to cover their arses… It’s fine, it’ll only ever reach those flow temps on a couple of days in deep winter.
My system was designed to the same 45deg flow temp, and for the last month has given a CoP of 6.5 and half the estimated energy usage to keep the entire house at 21deg.
ectoplasmosis
Soul
They designed for a very high flow temp (45deg) which would deliver a horribly inefficient COP.
I guess they have skin in the selling energy game.
This also meant they could underspec the radiators / change fewer of them.
In addition to the above, I had the following issues:
The person who dealt with my install throughout was incompetent, slow to respond and impossible to get on the phone.